Mppt and Shunt

Hello there,

I'm not sure if this is an issue or just me getting used to using this system full time.

I have the 100/50 blue MPPT and the 500a smartshunt. The smartshunt is showing my batteries are down at 32%, which with the weather could be accurate, however the MPPT history is showing that it entered absorption mode at some point during the day. Does this mean the batteries are actually much higher in charge than the shunt is telling me, or can the MPPT enter absorption for other reasons?

Any advice would be much appreciated.

MPPT SmartSolarSmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Mike Dorsett avatar image
Mike Dorsett answered ·

If the MPPT enters absorption during the day, this just means that the battery voltage measured by the MPPT got to the setpoint. This should mean the battery is 80% charged, but this could be affected by volt drop in the MPPT cables. What does the voltage trend of the shunt give for the voltage during the day? This could just be a synchronisation issue - if the shunt has not reached the sync voltage for several days or more.

20 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

karlosclaco avatar image karlosclaco commented ·
The voltage from the panels tends to stay steady throughput the day.

Is there a way to set the sync voltage or is that related to the absorption voltage?

0 Likes 0 ·
Show more comments
pwfarnell avatar image
pwfarnell answered ·

Where is the negative cable from the MPPT connected to the shunt / batteries, we see lots of people reporting that their SOC is falling because they have connected the MPPT negative direct to the batteries so the shunt never sees the charging current so does not count it. The negative from the MPPT must be connected to the "load" or "system" side of the shunt, not sure what it is called on the Smartshunt, the opposite side to the batteries.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

karlosclaco avatar image karlosclaco commented ·
The negative is connected to a busbar with every other negative, then goes to the load side of the shunt. I can see on the shunt when it's receiving charge by the wattage and Amps reading positively.
0 Likes 0 ·