question

sweyn avatar image
sweyn asked

Victron Lifepo4 never goes to float. Is this a problem?

My system is all Victeon. CerboGX, Victron Smart LiFePO4 200Ah, Multiplus, Lynx Smart BMS MPPTs etc and everything is controlled by DVCC so as far as I’m aware it should be self managing, but it just sits in Absorbtion from the Multiplus output once the battery is full.

Is this fine?

I’m worried that it will damage the battery to be constantly in Absorbtion for months on end.

BMSmultiplus ve.busfloat
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

@Sweyn

Yes, that's how it works. Just ignore that and look at the voltage rather than the charge mode. It is voltage controlled by your GX device.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sweyn avatar image sweyn commented ·
Ah, ok. I didn’t realise that it could change voltage within the mode.

Thanks!