I am setting up an ESS attached to the UK grid in my home. The battery has not yet been connected but will be a self-built 2S16P LiFePO4 system with 250 amp Daly BMS.
I am just testing things so far. The battery pack is not connected yet.
The only connections to the inverter are AC out 1 mains which is connected by a 4mm2 twin and earth to a small consumer unit with RCD and 2 MCBs, then back via that unit to my main consumer unit. Also, USB mk3 adaptor going to either a Raspberry Pi running venus OS, or to a tablet PC with VE configure.
Initially, I made an Earth link cable from the AC-1out Earth to the chassis earthing point inside the inverter but this instantly tripped the house RCD when power was connected. I removed that.
I have read the wiring unlimited guide and can see the purpose of the ground relay in off-grid and especially mobile systems where there is no guarantee that there will be a neutral-to-earth bond anywhere. However, in a stationary grid-connected system, there is always a neutral-to-earth bond by the utility so the unit never needs to connect the neutral to earth it will always trip the rcd.
I could turn the ground relay off in ve configure but when I set UK country code, this option ceases to be available. When I connect the power the unit closes the ground relay and the rcd trips.
Any ideas? In order to configure it I presently do not have the earth connected to the inverter - not ideal.
Is this anything to do with the battery being absent?