Multiplus 24/3000 label show AC Out 1 = 21 Amps
The documentation along with posts from others says it's about 70 Amps.
Please clarify...thanks.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Multiplus 24/3000 label show AC Out 1 = 21 Amps
The documentation along with posts from others says it's about 70 Amps.
Please clarify...thanks.
That's the inverter power (2400W / 115V = 20,8A)
70A is the transfer relay capacity + inverter power (Power Assist).