I have this setup:
- LifePoFe4 24V 560Ah wit JBD BMS
- Multiplus 24/4000/120, not on VE bus, on latest firmware version
- BlueSolar MPPT 150/60 (1500W solar panels), not on VE bus
- BlueSolar MPPT 150/35 (750W solar panels), not on VE bus
- 2000W solar micro-invertors on output,
- I allow feed-in to grid
- not using Cerbo or Venus; using VEConfig and VictronConnect app
Idea is to be ESS max self consumption. My problem is that with mains connected, it either feeds through the mains when high SoC(voltage) instead inverting and/or charges the battery from mains instead solar when low SoC (voltage).
I can do these satisfying functions, but not both together
1. PV inverter support (0180) always charges from mains input
2. ESS (017E) always feeds through mains input (even when > 28V or >90% SoC)
3. conditional AC input control (enables virtual switch --> disables assistants), ignores PV on output
As there is no bus, it can only work on voltage (SoC cannot be estimated by Multiplus), but I cannot configure in ESS (2) as I can do in conditional input (3).
Any suggestions? many thanks !
Fred