Expanding Multiplus standalone to 2x in Parallel

I'm about to expand my system from 1x Multiplus 24/3000/70-16 to 2x units in parallel, so I can have more inverter power. Currently, overload warnings/alarms come between 1800 ~2200 W depending on temperature.

I would like to ask community what are the important points to observe. I have read the manual, but is seems more focused in 3 -phase systems.

Things that I already had in consideration:

1. Ordered an unit that has similar hardware characteristics, informed that it was to match current unit

2. Ordered an MK3 so I can update my current Multi to same firmware version.

3. I will arrange a DC bus bar so both Multipluses see the same voltage from DC in

4. I will arrange an AC board so both Multipluses have same input and output AC wires lenght


5. Now my question: my current Muliplus is controlled remotely by the Venus, changing from GRID to Solar according with my needs. The Venus relay is physically connected to AUX1 of Multiplus, and I have programmed General Flag and Programmable Relay assistants to current Multi so I can change the operation mode (charger or inverter). Will I need to wire also the second Multiplus? I think so, but just to be sure. Any problem about this? Will they switch at same time?

Any other advice?

MultiPlus Quattro Inverter Chargerbattery charging
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

oxy avatar image oxy commented ·

> 1. Ordered an unit that has similar hardware characteristics, informed that it was to match current unit

That's actually pretty interesting - was it challenging to get a new MultiPlus to match your existing one? I'm having an issue where I need to add a second MultiPlus to double the power, but the dealer says ours is "too old" and its impossible to upgrade the software...

https://community.victronenergy.com/questions/18300/increasing-old-multiplus-5000-setup-to-10000-va-pa.html

My MultiPlus is at "1959143.VFD" version, what version your MultiPlus processor is?

Thanks!

0 Likes 0 ·
1 Answer
boekel avatar image
boekel answered ·
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Elimac avatar image Elimac commented ·

I have read that manual, as I said. It does not answer my question 5, does it? Do I need to connect both AUX1 relays to Venus or not?

0 Likes 0 ·
boekel avatar image boekel ♦ Elimac commented ·

Did you read this?
https://www.victronenergy.com/live/ve.bus:manual_parallel_and_three_phase_systems#assistants

It depends on what assistant you use, and you didn't specify which one you use...so I'd have to guess to help you...
Is it an ignore AC-in assistant? then I think only the master, as the units switch together.

0 Likes 0 ·