I'm just about to fit two Victron 305w panels in parallel. Do I need to fit blocking diodes anywhere in the circuit?

Solar Panel
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

if you are using the victron MPPT regulators then No as they already protect against feed back to the panels

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

christern avatar image christern commented ·
Isn’t it so that if one panel is shaded and the other is not in a parallel installation, there is current moving from the non-shaded to the shaded if no diodes are not installed?
0 Likes 0 ·
thesee avatar image
thesee answered ·

Yes 100/50. As I thought. I assume the panels have some sort of built in diode also. Thank you