So after a lengthy wait for some support on a parallel 48/5000 uk setup I am very disappointed with Victron Support.
I install these units as an Electricain. I have done so for some time now and know how and what there like as single unit setup's, They are good units.
But support has let me down on one of my customers installs.
They do not seem to accept there is an issue with a Parallel setup, grid set point is never achieved (mentioned on here a few times)
Also when in parallel you lose the normal fast response to get with single CT clamp setup.
When just using the Et112 the response is too slow, using an induction hob as an example, it just pulls from the grid and by the time the inverter responds the hob cycles and the inverter starts dumping to the grid!
After 2 weeks of escalating this is the response I got.
(UK Supplier)I think we are at the end of the road on this. The 'Official' line from Victron is
“The data you read is a calculated value and also with some deviation, it’s not scientifically to say the least
You can change the grid setpoint if you want.”
Disappointed to say the least and will not install these units with the impression on great victron support like I use too.