I have a blue solar mppt 75/15 charger connected to 200 watts PV and 5 110 amp hour flooded lead acid batteries. What settings should I use on the charger and how often should I equalise ?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I have a blue solar mppt 75/15 charger connected to 200 watts PV and 5 110 amp hour flooded lead acid batteries. What settings should I use on the charger and how often should I equalise ?
It's difficult to give a definitive answer on this. The settings vary between battery manufacturers and models. Please consult the documentation for your particular batteries as to charge parameters.
I'm a bit concerned that you don't have enough PV power to properly charge a battery bank of that size. I wouldn't expect to be able to Equalise that bank even at 200W in full sun. If your loads are very light then you might get away with it. In low light I don't think it will complete a full charge
Thanks for that. Usage is very light plus its backed up with a generator and an engine (its on a boat) so the charger goes onto float even in April s low light but that brings me to another question. If I stick on another 280 watts of solar can I buy an additional 75/15 and effectively run 2 independent systems charging the same battery bank instead of buying a much bigger controller and ditching the 75/15 I have. One of the reasons for wanting to do this is that the battery bank is split in two. " batteries at the front of the boat and 3 at the back 50 feet apart, linked by cables thicker than my thumb. Panels on the back of the boat are a pain in the neck so Id love to stick a couple on the front and charge the bank from both ends but will 2 controllers keep switching eachother in and out?
Additional resources still need to be added for this topic
5 People are following this question.
Large difference between solar blanket voltage output and Victron dashboard
Are 50vdc solar panels wasted on a 12vdc system?
SmartSolar MPPT 150/85 VE.Can - No current flow in Bulk with PV at VOC
BlueSolar 100/50 mppt controller shows "State" as "Off"
Why MPPT sizing system is recommending 150/35 and not 100/50 ?