The names for the digital inputs are all pre-defined but there is no option for , for example, 'Other'. Could this be added as there is a high probability that an input will be used for something that is not defined in the list - I can think of lots of possibilities.


Also, in the Modbus TCP register list, register 3424 Type the generator type 9 is missing.

cerbo gxModbus TCP
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
anieuwstadt avatar image
anieuwstadt answered ·

Try the following:

  • Choose input type: Settings > IO > Digital Inputs:
    • Choose type to select best match state options
      • Generator = Running/Stopped
      • Pump = On/Off
      • Door = Open/Closed
      • Alarm = Alarm/OK
  • Name the Input: Device List > Select Digital Input Device > Device > Name > Custom Name


1660200467221.png


  • Same applies to Analogue inputs.

1660201193710.png

  • Shows like this on the VRM Dashboard.

1660201238674.png



1660200467221.png (17.2 KiB)
1660201193710.png (18.4 KiB)
1660201238674.png (10.8 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Silvio Franceschini avatar image Silvio Franceschini commented ·

This is all very great, unfortunately in VRM alarms those names are not getting processed.

Just the alarm history page shows the custom name, even not in a very clear way.

In the alarm header and in the email of VRM there are just the generic descriptions.

Not very handy in case of a bilge alarm or burgler alarm, you / customer first have to login to VRM and go to alarm history to understand whats going on. (or yes, directly to Cerbo Remote-Console)

bildschirmfoto-2023-10-11-um-074503.jpg
bildschirmfoto-2023-10-11-um-074213.jpg

Kind of the same with relays. They can't be named at all, so no help for customer what relays is for what:

bildschirmfoto-2023-10-11-um-101417.jpg

0 Likes 0 ·
acuario avatar image
acuario answered ·

Ok, great, that works for renaming and giving a sensible name.

It's not reflected in the modbus data though. I selected Bilge pump (returns 3 in register 3424) and renamed my input to Fan. The modbus still returns a 3 as the Cerbo thinks it is still a pump type even though it's renamed.

I realise this is what is expected but I think if you can customise a name then you should be able to change its type number as well (for a custom one) as if you are using modbus then there is no way to determine the fan is not a pump.


Also, for whoever maintains the modbus register list, don't forget type 9 (generator) is missing.