The EasySolar goes to Sustain Mode. At 4:00 in the morning a bigger Load switches on (washing machine). The reason for Sustain Mode is the Battery Voltage? Best regards Thomas
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
The EasySolar goes to Sustain Mode. At 4:00 in the morning a bigger Load switches on (washing machine). The reason for Sustain Mode is the Battery Voltage? Best regards Thomas
Sustain, which Victron call absorption, is the fixed voltage part of a three or four phase charge cycle. Once voltage hits 14.4, AGM batteries are about 80% charged. Constant voltage completes the charge and current drops as it completes. Then the battery is held at a lower voltage, called float - charged, ready for action.
In ESS, sustain is triggered when the battery dips beneath the dynamic cutoff voltages.
What batteries are these?
How have your ESS cutoff voltages been set?
Have a read of dynamic cut-off in the ESS guide.
That large load may be setting it off.
I use the Victron 12,8V Lithium SuperPack with internal BMS. The Sustain Voltage in the ESS Wizard is set to 12,5 Volt. The "Entladeschlussspannung" (sorry in german) is 10 Volt. Do I have to adjust the Sustain Voltage in ESS Wizard to an other value than 12,5 V ??
There is also Peukert law in play
https://en.wikipedia.org/wiki/Peukert%27s_law
if you add your capacity with parallel batteries, discharge rate per battery will decrease and you voltage drops slower, hence you won’t trigget the sustain that easily.