ESS using Grid for no reason?

Hi my ESS uses Grid for no reason. Someone has an idea?

1659716348231.png

My system:

CerboGX
EM24
1x MP2 24/5000
8S3P custom Lifepo4 Pack with jkbms

My Grid setpoint is 80W

The room temp where the MP2 is is 27C

ESSgridess grid setpoint not reached
1659716348231.png (67.4 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
netrange avatar image
netrange answered ·

What is your max. Batt. discharge current? maybe 50 Amps ?


You have No PV ... The Rest is taken from the Grid ...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

mryoshii avatar image
mryoshii answered ·

where is this setting? In the bms its 200A but its not connected to victron.
And under DVCC i can only set charge current.

I also have seen 91A with my old 24/3000 MP2

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

netrange avatar image netrange commented ·

Es muss ja einen Grund geben warum er genau diese 50A zieht und nicht noch mehr.

Der MP2 24/5000 könnte ja wohl viel mehr ziehen als diese 50 ?!

Also denke ich mal das die Ursache hier liegen muss.

Dein BMS ist nur passiv, es schaltet also nur ab oder zu?


Ist die Inverterleistung im ESS Menü auf 1500 W limitiert worden


0 Likes 0 ·
Show more comments
jeanmarie avatar image jeanmarie commented ·
What was set as battery capacity in VE.Configure ?



0 Likes 0 ·
Show more comments