question

nam-erik avatar image
nam-erik asked

Energy Meter EM330AV5

Hi, can anybody tell me if the EM330AV5 Energy meter from Carlo Gavazzi is compatible to Victron. This is apparently the replacement for EM24AV5.


Thanks

Energy Meterem24
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
Juha Tuomala avatar image
Juha Tuomala answered ·

Their product listing page:

https://www.gavazzionline.com/CGNA/energy#!


1659612407965.png


What is interesting is that it has backlit display!


EM330 / EM340

• Dimensions: 3 DIN modules

• Installation: DIN-rail

• Backlit touch LCD

• Measurement of voltage, current, power,

power factor and frequency

• Bi-directional energy metering,

3x 8-digit, cl. B (EN50470)

• Measuring inputs

400 to 480 VLL AC, 5(6) A current

input via current transformer (EM330)

208 to 400 VLL AC, 5(65) A (EM340)

• Auxiliary power supply (EM330)

Self powered (EM340)

• Dual tariff management

• Pulse output or RS485 Modbus or M-Bus port

• Sealable terminal covers

• CE, MID (PFA and PFB), cULus (EM330)


Did not find single product page, maybe it's so new that they don't have it.


1659612407965.png (36.8 KiB)
2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Juha Tuomala avatar image Juha Tuomala commented ·

Product links

https://www.gavazzionline.com/pdf/EM330.pdf

https://www.gavazzionline.com/pdf/CTD-1XDSENG270907.pdf

0 Likes 0 ·
Show more comments
Juha Tuomala avatar image
Juha Tuomala answered ·

Does the "M-Bus port" stand for Ethernet with RJ45 connector? RS485 is probably twisted pair.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Juha Tuomala avatar image Juha Tuomala commented ·
Choosing 'Select product' and opening the 'Communications' dialog, there Ethernet Modus is red, unselectable. So this is only available with RS485 interface.
0 Likes 0 ·
Juha Tuomala avatar image Juha Tuomala commented ·

Nope, it's serial

M-Bus by screw connection. For communication of measured data M-Bus according to EN13757-1 0.3, 2.4, 9.6 kbaud

https://m-bus.com/documentation-wired/04-physical-layer

https://en.wikipedia.org/wiki/Meter-Bus

0 Likes 0 ·
Warwick Bruce Chapman avatar image
Warwick Bruce Chapman answered ·

Victron has confirmed that the unit supported is EM330DINAV53HS1X27


Note “27” at end


Got confirmation from Carlo Gavazzi, the suffix 27 on the part code means :

- Same communication protocol ( measured variables in reading mode in the same registers)
- 0.001 kWh resolution via Modbus RTU
- 3 DIN module
- touch key user interface
- 1 digital input (not for pulse counting)


I assume this means this unit has been designed specifically for Victron and that others will not work.


I’m still trying to find out if other EM330’s can be used in the meantime.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jjl avatar image jjl commented ·

Hi Warwick

Thanks

I cannot find any stock of the new supported Carlo Gavazzi EM330DINAV53HS1X27 which is supported by Victron. Can you point me point me to a stockist in South Africa. Thanks

0 Likes 0 ·
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

There is an updated datasheet, which lists the compatible CG meters, including EM330, EM340, EM530 and EM540 with model numbers.

4 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Warwick Bruce Chapman avatar image Warwick Bruce Chapman commented ·

Thanks Stefanie, the issue is that there are a number of EM330 models from Carlo but not all of them are supported by Victron.


Note the comment at the bottom of the table: "Selected models are supported. Ask your reseller."


Right now, resellers know nothing about this at all unless they're reading the release notes of Venus OS 2.90~ which is the only version that supports these meters.


In the release notes, we see the following:

Add support for new Carlo Gavazzi EM530 and EM540 meter. Sub-Family X and PFC is supported, part numbers:
EM530DINAV53XS1X
EM530DINAV53XS1PFC // MID Certification (European Certification)
EM540DINAV23XS1X
EM540DINAV23XS1PFC // MID Certification (European Certification)
<snip>
Add support for more CG Energy Meters. These meters count kWh like the ET340, which is unlike the EM24 and unlike most utility meters do. For more info that, see energy meter manuals. It can nevertheless be interesting due to shortages on the EM24. Meter model numbers (note the 27 suffix):
EM330DINAV53HS1X27 - November
EM330DINAV53HS1PFB27
EM340DINAV23XS1X27
EM340DINAV23XS1PFB27


By way of example, one of the suppliers in the UK which we have been talking to while we try find meters, suggested the EM330DINAV53HS1PFB. However, this model is missing the "27" suffix that Victron advises above we need to look for.

0 Likes 0 ·
Juha Tuomala avatar image Juha Tuomala commented ·
What is the difference between 3xx and 5xx series? @Stefanie
0 Likes 0 ·
Stefanie (Victron Energy Staff) avatar image Stefanie (Victron Energy Staff) ♦♦ Juha Tuomala commented ·

I don't know much about the difference between 3xx and 5xx (you can google this yourself by comparing datasheets straight from CG website) but what I can say is that the 5xx series has some advantages over the EM24, which afaik (because I still haven't gotten my hands on any of them yet) is:

  • Can be set up for net sum and phase sum calculation method (important for some countries)
  • It doesn't have the front selector anymore, which for some were quite a pain
  • Better terminal connectors
  • They are a bit faster
0 Likes 0 ·
Juha Tuomala avatar image Juha Tuomala Stefanie (Victron Energy Staff) ♦♦ commented ·
Is the net sum for negative values when doing grid feed-in? @Stefanie
0 Likes 0 ·

Related Resources

Energy Meter Selection Guide

Additional resources still need to be added for this topic

Energy Meter Manual EM24 RS485