Hi All here is my setup:
2 x Quattro 48/15000/200
1 x SmartSolar MPPT VE.Can 250/100 rev2
1 x 6kw Solis
3 x 200a/10kwh Rosen power wall with inbuilt BMS
35 x 390w panels (15 connected to MPPT & 20 connected to Solis)
I am told my panels are in strings of 5 on two separate roofs eg 3 strings of 5 making 15 panels on MPPT. I am finding that the 15 panels to the MPPT is roughly 25% of the output of the 20 panels connected to the Solis inverter. I am getting no response from my installer.
Both roofs are similar pitch and facing same direction there is no shading on either. The MPPT is always at around 25% of the solis inverter. Which is lower than what i had expected with a 5 panel difference.
Can anyone here help me understand if this is correct or suggest what i should look at?
Update: The company who installed have informed me the original installer has left them and a new engineer came out on 15th September. He confirmed that what i was told previously was incorrect there are 2 strings (6 panels and 7 panels) connected to the MPPT. He tested both and saw that both output the same Voltage and current to the MPPT. Disconnecting 1 string had no impact on the power generation of the MPPT but he could see voltage on the string when testing it.
I am now being told that they need to confirm that the MPPT has enough trackers to handle 2 inputs. I checked the VRM as to the exact model of the MPPT:
I do not understand what is meant by trackers as this appears to be the largest MPPT Victron offers and has enough input ports for more strings to be connected than the 2 i have connected. This seems to confirm that I am generating 50% of the power due to 1 string not being used but the question remains how can this be fixed?
Thanks