Grid Loss even thou the grid is available (Multiplus(s) in parallel)

Good Day,

I have an issue with my setup going into inverting mode even thou the grid is available , i also noticed that even if the is no ac loads the vrm reads a value between 30W and 40W, using ve config the units have no errors:


My setup overview :

3 Multiplus in parallel

FW version : 497

1 250/100 MPPT

6 Victron 220ah gel batteries .

GX Color control .

Im using an assistant HUB-1 keep batteries charged feed surplus back to grid.

@Guy Stewart (Victron Community Manager) please can you advise.

state.pngfw.pnggrid.pngac-loads.png


Regards

gridmultiplus in parallel
grid.png (20.1 KiB)
state.png (24.0 KiB)
fw.png (18.1 KiB)
ac-loads.png (55.1 KiB)
5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
nickdb avatar image
nickdb answered ·

It is behaviour I see regularly here when the grid is under strain, voltage within the limits but the system starts inverting. When the grid stabilises everything returns to normal.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

denzel avatar image
denzel answered ·

Update: I have checked the N - E voltage and they with in 1.9V . This morning again around the same time with no loads the system had a grid loss alarm again. 3 times. I now changed from "HUB-1" to an ESS mode to determine if this is related to a config issue.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

denzel avatar image
denzel answered ·

Hi Guys,

I found the issue relating to my grid loss problem. The was not on the Grid side but a setting on the Master Victron unit . The AC High Disconnect Voltage was set to 240V and my grid at time suppled 242V which then the Multiplus disconnected the AC until the Grid went down to 235V .


Had the Victron alarm alert reported something like "AC Input Volt High" instead in "Grid Loss" we would have found the issue much faster.

Still a very good feature to have .

"The setting is found under the Grid tab in VE Config"

@nickdb @Alexandra thank you very much for your assistants in this matter.

Regards


Denzel