When i set my discharge floor on 50%
And the geneator autostart stop on 0%- 100%.
Will the 0% actual be 50% or would i completly discharge my battery bank to 0%?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
When i set my discharge floor on 50%
And the geneator autostart stop on 0%- 100%.
Will the 0% actual be 50% or would i completly discharge my battery bank to 0%?
@Marc Heide , The discharge floor is set on the smartshunt to allow the smartshunt to tell “time to go”. It has no other function.
The generator start SOC sets when the generator will start. In your case you will start the generator at 0% SOC and stop the generator at 100%. We would not set it like that because while you can discharge lithium batteries completely it does reduce their cycle life. We would set generator start to maybe 20% and stop the generator at say 98%.
The discharge floor and generator start SOC do not interact at all and serve different functions.
Regards,
Trevor
Thank you guys.
Now i know there is no interraction between the settings!
Pa. I now never to discharge to 0% but it was just for an example.