question

padamson1 avatar image
padamson1 asked

MPPT has stopped fully charging 48v bank

I've had a MPPT 150/45 hooked up to 48v bank which two banks of two 100Ah 24v LFPs (400Ah capacity) functioning fine for 7months. The MPPT would increase voltage until absorption (58.6v) about every other day this month and properly drop to float.

Starting last week, right after a firmware upgrade from my phone, the MPPT output voltage never goes above 53.9v. Battery temp is 33c so it is not a thermal shutdown. It slowly gets to 53.9v and just stays there, pumping in 500-750W for the rest of the day. The SmartShunt reports 100% at 53.9v which is different, but if I manually reset the SmartShunt SoC to 90% using Victron Connect it will go to 100% at 53.9v even though voltage hasn't gone over 57v. Looks like the SmartShunt is just measuring current flow into the battery for SoC.

No wires have changed since this weirdness started, only firmware. I also have a 24v bank connected to different MPPT 150/45 which functions as before and goes above 27v as soon as the batteries are 26.8v (according to Smart battery readings) and the voltage continues to climb until absorption (28.6v).

The strange thing is the firmware version on the 24v MPPT says v3.10 on the Product Info page, but the 48v MPPT says v1.59 (and that it is the latest version). If I click update, it says that I have the latest version. Huh? Why is one version different than the other?


Anyone have thoughts on what is limiting the MPPT output voltage to 53.9v?


screenshot-20220725-080357.jpgscreenshot-20220725-075220.jpg

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
nickdb avatar image
nickdb answered ·

There are different hardware revisions which run different firmware, so the versions won't match between models and ages of product.

Have you double checked none of the settings were overwritten by the update and that charger settings are as you expect them to be?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

padamson1 avatar image padamson1 commented ·
Yes. I only used the switch settings. So 48v, 45a, and switch position 7. The load output is on battery life. However I now remember being forced to enter a value when I first brought up the MPPT pages after the upgrade, but I can't remember what it was and don't see anything I new on any of the settings pages.
0 Likes 0 ·
JohnC avatar image
JohnC answered ·

Hi @padamson1

v3.10 is for a CAN port equipped mppt. You could check, but these updates are very reliable.

The real clue here is that the batts are still accepting charge. Possibly a phantom load, or to heat (that'll be noticeable). The most likely scenario is that the Smartshunt is incorrect. The batts should reach 100% when they can't accept charge at Absorb V. Maybe accumulated drift or regular premature syncing. Can you screenshot it's settings? For now, assume that it's wrong.

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

padamson1 avatar image padamson1 commented ·

Somehow my response seems to have disappeared.

Below is the settings for the SmartShunt. The SoC can be ignored b/c I manually set it yesterday when the 48v MPPT clipped at 53.9v to see if the Shunt was causing the the clipping. Knocking the SoC down to 90% increased the consumed Ah but the voltage did not move past 54v on the MPPT.


Right now the 24v MPPT output is 27.05v and the batteries read 26.75v (on VictronConnect), but the 48v MPPT output flutters betweem 53.8 and 53.9 while the batteries read 26.8 That small differential on the 48v MPPT seemd too low to get current into the 48v batteries to me.

screenshot-20220725-094628.jpg


screenshot-20220725-094517.jpg

0 Likes 0 ·
Show more comments