Hi,
Can anyone clarify the highlighted comment attached?
" When the battery current is low enough the contactor will open so that the DC system is disconnected from the batteries"
I have tried to carry out a few initial tests, but get varying results. When no load is present (on the outgoing contactor terminals) and the Rem On/Off is opened, the safety contactor opens immediately (as expected). If I generate a load (e.g. a Quattro inverting with 2-3kW), the contactor can take anywhere between 5 and 20 seconds to open. Presumably the BMS 500 isn't intelligent enough to command external loads (such as a Quattro/Multi) via VE.Can -> Cerbo -> VE.Bus, so how will the shunt determine what is an acceptable current level to open?