Is it time to replace my controller?

I have two 100/50 controllers connected to my AMG domestic battery bank. Checked all of the connections, taken the entire system off line over night....

I still get these erroneous readings from my Port controller. (Yes I checked the voltage directly at the battery) Looking for suggestions

.

MPPT Controllers
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
wkirby avatar image
wkirby answered ·

I wouldn't have thought it's time to replace the controller. It could be down to a bad connection somewhere between the controller and the battery. I assume both controllers are charging the same battery bank?
This is just the symptom a poor connection would present.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

emmykate avatar image emmykate commented ·

Yes there was poor contact at the fuse... cleaned it up and seems to be working.

Thank you