know enybody how setup discharge current battery limit? becouse i think is important and missing thanks
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
know enybody how setup discharge current battery limit? becouse i think is important and missing thanks
There is no such setting. Basically you have to limit the loads.
If using ESS you can limit the inverter power (and "top up" from the grid if the loads are larger than your limit), but that limits the power drawn from battery and/or MPPT charger(s), not strictly from battery.
this is unhappy, and is prepare this function in future? I dont uderstand why that basic function is missing. thank you and have a nice day
Do you want to limit the current flowing out of your battery?
Or limit the depth of discharged for your battery?
thank you
Yes, exactly I want to limit the current flowing out of battery and can not limit power of multiplus, becouse during the day battery and mppt gíve together more power. Battery have a capacity but have not so many current.
I was able to do this - see my answer to Question 66801.
I have the same concern as my battery specification has a 90A limit.
But I can't seem to find answer to question 66801. I can't find question numbers...Would you mind putting me in the right direction?
@Philippe Rigollet This is 66801..
https://community.victronenergy.com/questions/66801/index.html
Related to exporting power. It's not possible to limit battery power to standalone loads, as it would only damage the loads