Hello,
I've configured my Pylontech, MultiPlus, ESS etc. as mentioned here: https://www.victronenergy.com/live/battery_compatibility:pylontech_phantom
It's a three phase system, 6,4kwp solar, with 2 mppts. 14,4kwh Pylontech...
It worked for months without problems. Now it won't "fully" charge the battery. Only when it's SOC is very low it charges till round about 60%SOC. As you can see in the picture it feeds back to the grid although the charge limit allows more current to charge into the batteries.
When I turn off the Multis and only the mppts are active the battery is charging well.
I have switched on the "2nd Batterymon from the Multi" in vrm and as you can see, the SOC and Voltage of the Multi-Bat-Mon are to high. Therefore the Bulk Phase is very short (in this time the batteries are charging with their max Current), then there is the Absorption Phase and the charge current goes down and the feedback goes up. Unfortunately I don't know whether this "Voltage Difference" was from the beginning.
I've measured the voltage on the multi and it's the same as measured from the Pylon BMS.
Now I've updated all Firmware to solve the issue, but it doesn't.
What should I change to make it work again?
Summary:
At all points of the installation (pylon, multi, MPPT connector) you can measure the correct and equal voltage using a multimeter. If you connect to the MPPT via Bluetooth and the Victron app, then you see that this measures the too high voltage. I assume that this wrong (too high value) is also taken in the ESS and therefore the regulation does not work properly.
Sorry for my bad english...
Thanks
DavRey