Has anyone got any suggestions here as to how to fix this or what to try, We have had this reported to victron service now for over 4 weeks, with no resolution.
The below pictures are showing a screen on the customers Cerbo (fw 2.87) - we have also tried without the multi control being connected. Please NOTE the The AC out amps reading as its incorrect by a large amount however the WATTS reading is correct.
This display error also shows the same figure on the tiles.
Of note is that if we turn the two units off for 30 min then power back on the error is resolved sometimes for 1 to 2 days then the issue reappears. and it does not mater if AC1 in or AC2 in is used as the power source
We have replaced BOTH cerbos with two more brand new units same issue. Also even if the Cerbos are disconnected and only the Multi control is connected the amps limit is always out by the variance in the output ac1 amps reading.
The above show the AC amps being incorrectly displayed HOWEVER the watts reading is correct.
2 x brand new Quattro 24volkt 8000 units using 497 firmware also the VE.BMS selection has been selected. both connected in Parallel.
Of note this boat has 2 full sets of these quattros (4 in total) AND BOTH SETS SHOW THE SAME PROBLEM
Please see the attached pictures - this error only occurs if the units are in Parallel in stand alone mode they work fine, and sometimes it only shows up after a few hrs of usage and the in balance varies
The amps reading error then causes the AC amps limit to be incorrect by the amount of the reading error.
If you turn off the incoming ac source then the outgoing amps reads correctly, see picture below
OTHER Pictures Below