Fuse size between battery and Multiplus inverter

I have a Multiplus II 5KVA and 3 x 3Kw 48V Pylontech Lithoum batteries.

Multiplus II 5KVA with 48V battery has a maximum power peak of 9Kw.

Does the fuse between the battery bank and the invertes have to be size for the nominal current (104A) plus a 25% security factor or for the maximum peak current (188A) ?

Thanks


Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

There should be a fuse size in the manual. But it needs to be sized above peak. Same goes for cabling.

The startup current with the big capacitors inside is very high.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·

I just checked the manual. Section 4.2 says 200A fuse, 70mm square cables up to 5M, 2*70mm over that.

Use good quality maxi fuses.