DC loads/DC system in ESS

Hello,

I have a 3-phase system 3x5kVA MPII, 1xMPPT, 2xFronius Symo, BMZ lion battery 48V with BMS, everything is controlled by Cerbo + ESS assistant. Everything has current FW, AC Coupled feed in excess - ON, DC Coupled feed in excess - OFF. Now I canceled home UPS APC (for home server, CCTV...) installed Phoenix inverter and SmartShunt. I turned it on in Settings - System - Has DC system ON. I set the SmartShunt as DC Loads. Unfortunately, I have two problems.

The first problem - the DC loads field does not appear on the display. It only appears immediately after a restart, or on the display that I'm not using.

Normal view ( No icon DC Power displayed ):

1657135112049.png

Display after restart Cerbo: (as soon as ESS assistant starts, the DC loads field disappears)

1657135112106.png

Another screen I don't use, here is the DC loas to see:

1657135112156.png

Would it be possible to modify the FW to show the DC load on the "primary" screen like here?

1657135112185.png

The second problem - if the battery is charged, CCL 0A. When I turn on the DC load, the battery discharges and micro-cycles (100% -> 97% -> 100%...). Unfortunately, the MPPT does not supply any power (to balance the draw from the battery), the Symo supplies power to the grid. Is this normal behavior? Shouldn't the MMPT regulator supply the same power as the Phoenix draws so that the battery is not constantly being discharged and charged? It can be seen in the pictures above.

Thank you for the responses, or for the advice.

Ondra

dc system
1657135112185.png (57.6 KiB)
1657135112049.png (289.0 KiB)
1657135112156.png (226.0 KiB)
1657135112106.png (265.9 KiB)
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

ronski avatar image ronski commented ·

I also have the same problem, DC loads was displayed, after I added the ESS assistant it disappeared.


Actually this could be the cause https://community.victronenergy.com/questions/86449/dc-loads-not-shown-on-screen.html they also have ESS enabled.

0 Likes 0 ·
Show more comments
2 Answers
janr-1 avatar image
janr-1 answered ·

Hi,

Did you find a solution in the mean time?

I have exactly the same problem with "DC-loads" (an external charger in my case). DC-Loads are visible directly after booting the GX, but they disappear once ESS has started.

My GX (MultiPlus 2 3000 GX) has firmware 2.89.

Greetings,

Jan

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

zonnigbreda avatar image
zonnigbreda answered ·

Replying to old topic, as per the latest software this is still a very annoying issue.

Is there any hint on how to fix this?

Can this be fixed by a guimod or is it not calculated by the system?