Miltuplus II - charging from MPPT no to ac loads

Hi

I am newbee in Victron, have Multiplus II-GX. I have one question, system is set to ESS with little feed-in and SOC for battery was set to 20%, i have small problem in the morning where i have some power from MPPT but its used for charging the battery not to use it for AC loads. AC loads are fed from grid (for money). How can I set system to use MPPT and battery to fed the AC back again? It worked at night (using battery not grid) until SOC drops down to 21%.

snimka-obrazovky-2022-07-04-o-80843.png

Multiplus-II
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
lifeingalicia avatar image
lifeingalicia answered ·

Set a scheduled charge e.g. 7 - 9 with SOC 20.

Scheduled charge will use AC/PV up to the desired SOC then charging will stop but NO charging & discharging of battery till end of schedule.

Thus any PV is used for AC or fed back.