I would like to know, in an off-grid scenario, will changing the MP2 output voltage affects its total capacity (VA)?
Reason I ask, is that usually the internal electrical componts are limited by current (A) and not Watts. They can take their rated Amps as long as they operate within their operating voltage.
So let's say a 5000VA inverter is designed to run at 230V and will support:
5000 (VA) / 230 (V) = 21.7 (A)
Can I then correctly say that if I put the inverter output at 210V my total output would be:
21.7(A) * 210(V) = 4557 (VA)
and the same for a higher voltage
21.7(A) * 240(V) = 5208 (VA)
Is my understanding correct or does Victron work differently?