Solar chargers don't work under ESS

Good day,

Two solar chargers Smart MPPT 150/70-Tr and Smart MPPT 250/70-Tr don't charge the batteries under ESS mode. On VRM the system shows this:

1656266265421.png

I have set the system to not sell any PV excess to grid. However if I set the system to sell the excess, controllers do start to charge and export PV excess to grid:

1656266381736.png


Moreover, if we disconnect the VE.Direct cable from both controllers to Venus GX, they do charge battery bank but system doesn't run under ESS:

1656266534076.png

Any clue of what could be wrong on configuration? I need to set the system up properly for ESS and I have compared all parameters with other systems I have installed that seems to run properly on ESS.

Thank you in advance for your help.

MPPT ControllersESS
1656266265421.png (178.6 KiB)
1656266381736.png (188.4 KiB)
1656266534076.png (21.0 KiB)
7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·
In situation from the first image, if you disconnect AC In, does the MPPTs start to provide power?


What else you have in that system?


Maybe put some screenshots with some of the settings.

1 Like 1 ·
dgmar-ni avatar image dgmar-ni seb71 commented ·
Here are some screen shots for the system's configuration...
0 Likes 0 ·
seb71 avatar image seb71 dgmar-ni commented ·

Can you try this:

In situation from the first image, if you disconnect AC In, does the MPPTs start to provide power?

With the VE.Direct cables connected between the MPPTs and Venus GX.

0 Likes 0 ·
dgmar-ni avatar image dgmar-ni seb71 commented ·

It does not:


1656351866657.png

AC In disconnected but charge controllers don't work.

0 Likes 0 ·
1656351866657.png (237.5 KiB)
dgmar-ni avatar image dgmar-ni seb71 commented ·

I just changed the firmware version for the Quattros and now is working running on solar:

1656352702135.png

The firmware version is 433:

1656352753819.png

The ESS doesn't work with the latest version of the Quattros.

0 Likes 0 ·
1656352702135.png (35.3 KiB)
1656352753819.png (7.5 KiB)
duto69 avatar image duto69 seb71 commented ·

in my case, if I disconect AC MPPT start charge. Do you know, where is problem?

0 Likes 0 ·
dgmar-ni avatar image dgmar-ni commented ·

Device list:


1656275246912.png

1656275265951.png

1656275284806.png

1656275434256.png

1656275451025.png

Both charge controllers have been disconnected as you can see they have more than one day since last connection.


0 Likes 0 ·
1656275246912.png (16.8 KiB)
1656275265951.png (9.3 KiB)
1656275284806.png (7.2 KiB)
1656275434256.png (8.5 KiB)
1656275451025.png (8.6 KiB)
6 Answers
dgmar-ni avatar image
dgmar-ni answered ·

It turns out that I didn't realize when I changed the firmware version the ESS assistant was removed. But once I installed it It didn't work. So again this is the behavior now without rhe ESS assistant:

1656357430605.png

1656357475768.png

1656357499888.png

But no ESS assistant installed:

1656357549318.png

I have updated everything all devices to latest firmware. What is the proper assistant to use?

1656359338018.png

ESS (Energy Storage System)(017E) didn't work for this firmware version:

1656359421826.png


1656357430605.png (33.3 KiB)
1656357475768.png (55.3 KiB)
1656357499888.png (37.3 KiB)
1656357549318.png (11.2 KiB)
1656359338018.png (146.6 KiB)
1656359421826.png (6.7 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dgmar-ni avatar image
dgmar-ni answered ·

I have reinstalled the ESS assistant and seems to be working now:

1656361117263.png


1656361117263.png (34.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dgmar-ni avatar image
dgmar-ni answered ·

Settings on remote console:

1656275679156.png

1656275713898.png

1656275781498.png

1656275819777.png

1656275859668.png

1656275911698.png

1656275940275.png

1656275971958.png



1656275679156.png (40.4 KiB)
1656275713898.png (39.2 KiB)
1656275781498.png (46.2 KiB)
1656275819777.png (35.9 KiB)
1656275859668.png (26.0 KiB)
1656275911698.png (36.8 KiB)
1656275940275.png (36.9 KiB)
1656275971958.png (40.6 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Matthias Lange - DE avatar image
Matthias Lange - DE answered ·

What batteries do you have? What are the charge settings of the MPPTs(VictronConnect)?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image
seb71 answered ·

The charging settings in the MPPTs must be fine since they are charging when the VE.Direct cables are disconnected from Venus GX.


Can you post screenshots with the charger settings and ESS settings from Quattros?


Also, disable "Has DC system" from Venus GX settings.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image
seb71 answered ·

DVCC is enabled?

What is the charging current set there (if enabled)?

2 |3000