Multi RS Solar uses Grid instead of PylonTech and Solar panel

Hello Everyone,

in my father's house I have installed the Multi RS solar on PylonTech barltteries. thanks to other users in the forum I have managed it to make it running. if there is consumption on the deducted AC output, unfortunately the system prefers to switch directly to the grid and ignores the full batteries. only if ACin is switched off and the system is disconnected from the grid, it switches to the batteries.

I can imagine that this mode makes sense in mobile homes or in a boat. In my parents house it makes no sense this way and I have to put down the fire manually each time I want to use the batteries.


is there a setting that I haven't seen in the software? can someone please give me a hint?


thanks again to the community!

Elmarimg-20220602-210651.jpg

gridsmart solar charging behaviourrs inverter
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·
3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

seb71 avatar image seb71 commented ·

Unfortunately ESS can't be used with Multi RS.

0 Likes 0 ·
shaneyake avatar image shaneyake commented ·

Unfortunately the Multi RS is not the right inverter for this application.
A Multiplus-II would be the correct inverter for this application.
However you should be able to tell the Multi RS to disconnect from grid when at high SOC and reconnect once the batteries are low. I would try the Victron Connect APP to see if you can setup ignore AC.

0 Likes 0 ·
mondeoman avatar image mondeoman shaneyake commented ·

"reconnect once the batteries are low" the problem is it will start charging the batteries from the grid as soon as it switches to the grid. So in the morning, when the sun comes up, batteries are already full with grid electricity.

0 Likes 0 ·
mondeoman avatar image
mondeoman answered ·

I have also asked if the Multi RS can be used for a solar self-consumption system and I did NOT get an answer. Solar self-consuption requires disabling the grid charger so that the inverter would not charge the batteries from the grid when switching to grid.
But I did find some ambiguous information that the Multi RS might actually support some form of embedded ESS.

See here: https://community.victronenergy.com/questions/121388/multi-rs-solar-hybrid-self-consumption-optimizatio.html

9 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·

@MondeoMan

@Elmar Streich

Only VE Bus products can do ESS.

The Multi RS is not a VE Bus product so cannot be controlled like that.

The features being searched for are found in the fuller featured Multi 2 as mentioned above.

See ESS manual here.

0 Likes 0 ·
mondeoman avatar image mondeoman Alexandra ♦ commented ·

@Alexandra Look at the screenshot posted by "ubi" on the topic linked above.

It clearly shows ESS being set up via VictronConnect.

33862-multi-rs-solar-ess-menu.jpg

0 Likes 0 ·
Show more comments
semlohnhoj avatar image
semlohnhoj answered ·

I've just ordered the Multi RS Solar to use in a hybrid system. I want it to use batteries unless the load is too high for the inverter and then supplement it with the AC input. I know the MultiPlus-II has "AC input control" which seems to achieve this but is this not possible with the Multi RS Solar? If not then is this product just a glorified UPS? I might be tempted to cancel the order if that's the case.