question

simon-jukes avatar image
simon-jukes asked

Muliplus 2 48/5000/70-50 and Pylonteck UP5000 batteries

Hi all

Looking at installing a Multiplus 2 48/5000/70-50 with Pylontech UP5000 units. Reading the following it seems the minimum number of US2000C batteries is 4 for a 48/5000. It's going to be configured as a ESS system with no essential loads

Victron & Pylontech UP2500, US2000, US3000, US2000C, US3000C, UP5000, Phantom-S, Force-L1 & L2 [Victron Energy]

I have a 4kw PV, AC tied which is an East / West split so it never goes above 2.2kw of PV at anyone time, however, at some point I may add another 2 * 375w panels to a MPPT charger

Is it ok to start off with 2 UP5000 batteries on this inverter and add a 3rd / 4th later?

By my calculation I need at least 3 UP5000's, each one's surge discharge is 4320 watts so 2 only gives 8640 watts where the inverter max surge is 10,000 watts

Edit. looks like my info for the 5000 was incorrect, looks like the surge discharge is actually 120-200 amps which is 5760w - 9600w, so, in theory, 2 UP5000's should be fine

Anyone installed this inverted with only 2 UP5000's to start with - any problems at all?

Thanks




Multiplus-IIESSPylontech
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
cordy-van-der-burg avatar image
cordy-van-der-burg answered ·

Hi,

I'm running the MultiPlus II 5000 with 3x Pylon US3000C, which is 10,5 kWh, you're planning to run 10kWh which should be just fine.

Best regards,

Cordy

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

simon-jukes avatar image simon-jukes commented ·
Thank you
0 Likes 0 ·