Main Grid Failure Alert when Inverting

Can someone tell me why I get a Main Grid Failure Alarm when the Multi goes back and forth from an 'Ignore AC' condition.

Periodically, when the Multi is inverting (but connected to grid) and dedicated AC Ignore is selected in VS tab I get a Grid Failure Alarm. But the grid hasn't failed and VS functions properly, switching between Inverting and passing through Grid AC when conditions are met. In VRM portal dashboard system overview, the Grid box will show ' - ' when inverting, which I figure is normal since it's not drawing any current, but it's odd I keep getting a Grid Failure alarm. Is this the Multi's current sensor mis-reading things or is there a setting I missed somewhere? Thanks!

screenshot-2022-06-21-183630.jpg


Multiplus-IIVRMsensorvirtual switch
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·
@Duswami

Because you are disconnecting from grid with ignore ac. So technically the connection is lost. It is really a warning to let youknow you are inverting again.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duswami avatar image duswami commented ·
@Alexandra Understood thanks
0 Likes 0 ·
Alexandra avatar image
Alexandra answered ·

@Duswami

Check on your GX device you can enable or disable it there.

Menu - settings - system setup - monitor for grid faliure.