question

scottd avatar image
scottd asked

Esy Solar 12 1600 MPPT Solar panel layout Wiring

Hello All, Thank you so much for all your help. I am super excited to get stuck into my new project and switch to an awesome Victron System. I have on order an Easy Solar 12 1600 and just have a question on panel layout. I have ordered 4X https://au.renogy.com/renogy-200-watt-12-volt-monocrystalline-solar-panel/ and wanted to find out my best options on wiring them to my 2X 200ah 12V Litium Batteries that will be in Parallel configuration. Am i better to have the panels in Parallel or series configuration to the Easy Solar input. Also can these 4X panels be plugged into just one of the 3 input plugs for the MMPT on the easy solar?

EasySolar All-in-One
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
scottd avatar image
scottd answered ·

@klim8skeptic Why would i bring 2 does in series and 2 down in parallel? Am i missing something? If i use series won't the MPPT convert the extra volts to amps and flow that through to the batteries? You have confused me with your post.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

klim8skeptic avatar image klim8skeptic ♦ commented ·

An example of a 2 Series X 2 Parallel array from Wiring Unlinited.

2-series-x-2-parallel-array.png

With your panels you will have 2 strings of 2 series panels.

Array Voc of about 54v, and Isc of 19.32a. Well within the mppts input rating of 100v-60a.

0 Likes 0 ·
klim8skeptic avatar image
klim8skeptic answered ·

2 Series x 2 Parallel array would be good. This can be done without series fuses, although a breaker would be nice before the mppt.

You could use Y connectors on the roof and only bring down 1 pair of wires to the mppt.

Or you could bring 2 pair down and join at the breaker.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image kevgermany ♦♦ commented ·
@ScottD if you bring a single pair of wires, this must be 4 panels in parallel. Otherwise you'll blow the charge controller with 4 panels in series.

The 3 pairs of MC4 connectors on the easysolar are connected in parallel to the charge controller.

0 Likes 0 ·
Show more comments
scottd avatar image
scottd answered ·

Thanks Guys for your time and replies. @klim8skeptic The picture is 100% clearer now i understand. I think that's the configuration i will go with. Thanks for your Time! :)

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.