Am I understanding correctly the grid AC passes through the Multi AC1 OUT when the inverter is in charging mode ONLY?
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Am I understanding correctly the grid AC passes through the Multi AC1 OUT when the inverter is in charging mode ONLY?
It is one of the instances. When using the system as a backup system it will too as well as when pulling in power from the grid to make up an inverter load shortfall when in ESS self consumption mode.
@ejrossouw ESS aside, since I'm not using it will it pass through AC automatically (to make up for a load shortfall from the pv or bats). For example, when DC coupled PV is insufficient will it automatically pass through grid AC if present or does that scenario need relays or assistants (not ess)?
So, now, if I want to 'supplement Grid' AC with DC coupled PV, what's the best method since I'm not using ESS, looks like Generator Asst is for PV coupled only.
If you want to supplement GRID with DC PV you need to use ESS, this is the whole point of ESS.
You can trigger ignore AC which will disconnect the inverter from Grid and use Battery and PV to run loads but without ESS you can't use grid and DC PV at the same time.
Depends on your utility but you can use Other which will allow ESS.
As kevgermany said you can set input current low, 6A is the min on most inverters and then enable Power Assistant this will active the inverter whenever you draw more than 6A from grid. So would kinda work.
Where in the US are you? MN has a nice program to certify non UL listed installations for Grid export.
@ejrossouw @kevgermany @kevgermany So basically I have this done. Is there a way to make AC Ignore conditional on the presence of PV only. For example, AC Ignore condition applies when PV is available, but AC Ignore conditions are 'ignored' when there's not PV.