I want to add a low SOC alarm, but it seems to require a high SOC alarm too. I don't want constant alarms about the batteries being in a good state, just when they are lower than I prefer and might not be paying attention. Thanks, Bill
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I want to add a low SOC alarm, but it seems to require a high SOC alarm too. I don't want constant alarms about the batteries being in a good state, just when they are lower than I prefer and might not be paying attention. Thanks, Bill
Which device are we talking about? Are there other components in the system that could play a role in this? If so, please mention them too.
I want to setup a Low SOC alarm on the BMV-712 via VRM. Just want an alert if the state of charge goes lower than I usually want to keep it above. I just cannot see a way to leave the High SOC alarm inactive. -Bill
Hi @bigbillsd,
This is probably not intended. But maybe you can trick the system by using a value for 'High' and 'Clear high alarm' that cannot be reached and thus overrides the 'High' alarm rule. Give it a try.