ESS for peak-shaving only, require valid grid code in US?

I've heard a lot of back and forth on this topic, and it seems using ESS to feed back anything to the grid certainly does require a valid grid code selection, and is technically not legal in the US therefore.


What I am trying to find out now, is if the use of ESS for peak-shaving only is permitted, without any grid feed-in, and no PV connected on the AC-Out side of the MultiPlus. This forum here discuses the topic at length, and read some people claim that yes ESS can be used as long as there is no feed-in happening, but wanted to get some sort of official clarification from someone who is licensed here in the US maybe and has done such an install:

https://community.victronenergy.com/questions/15997/quattro-120240-selling-to-grid-in-usa-which-countr.html


In the state I am looking at having this installed (Oahu), electricity can be billed based on the time of day, costing as much as $0.52/kwh at night, and as little as $0.25 or so during the daytime, due to the excess of clean solar, and high cost of importing fuel to burn in power plants. Furthermore, I am living in an apartment-style condo where I do not own the roof above me, and cannot install any solar of my own.


In my scenario, ESS would be used to power the loads on the AC-Out side during the night time, and recharge from the grid connected to the AC-Input side during daytime. The batteries would never be discharged back to the grid, as I would not be credited for this anyhow. However, I have read that when the MultiPlus is inverting, powering a heavy load like an electric water heater - the load which would shut off abruptly at times, causing a small amount of energy to possibly be sent back out the AC-Input side, if even for a few milliseconds. Would this not then cause the installation to be illegal due to the lack of grid code compliance in the US?

ESSusa
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·
@ee21

Since this is an international forum, it may be best to contact a local dealer /installer for more regional regulation questions.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image
wkirby answered ·

You need to have a grid code set in order to enable ESS.

However, you don't need ESS to do what you want to do. If you are powering all of your loads from AC-OUT then that's fine. Then you simply disable the AC-IN relays for the expensive times and then enable the AC-IN relays for the cheap times when you want to charge.
The hot water need not be connected to AC-OUT of the MultiPlus, you could simply have it wired to the regular main supply and have a separate relay or timer to set it to heat during the cheap times.