Which Relay assistant for Conditional AC, DV switching

I want to program some relays in the Multi II for conditional AC, DC usage instances and am confused as to which assistant/relay I should use, the programmable relays, general Flags or AC-related relays. The conditions I'm trying to set are as follows:

  • If MAIN AC and SOC is greater than 98% and PV is greater than 100W then use PV for loads, when not enough PV use Bats to 75% SOC
  • If MAIN AC and BAT SOC less 75% PV Charges bats to 100% SOC and use 100% Grid for loads
  • If Main AC and PV is less than 100W then charge bats
  • If Main AC and no PV use Grid
  • If no Main AC and SOC is greater than 98% and PV is greater than 500W then use PV, when not enough PV use Bats to SOC 55%
  • If no Main AC and Bat SOC is less than 55% use PV to charge to 100% SOC, don’t use Bats for loads
  • If no Main AC and PV less than 500W charge batters to 100% SOC
  • If no Main AC and no PV Run loads on Bats to SOC 55%

* Note: in the instance of no MAIN AC, AC OUT 1 is the only source of AC to essential loads.

For PV conditions, should I use W or VDC? I'm more interested in utilizing the PV when requisite Watts are available as the system generates between 85-75 VDC between sunrise and sunset.

If anyone could kindly take me through an example routine step-by-step, or screenshot their own so I have a model to work off of I would appreciate it! Any tips, suggestions or helpful hints would be great too. Or, if there is an easier way or a better method to condense these to achieve the same result feel free to let me know. Not using ESS btw. Thanks! :)


Multiplus-IIbattery chargingRelay
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Alexandra avatar image
Alexandra answered ·

@Duswami

You will really only be able to ise SOC and load based controls on the AC conditions to connect or disconnect.

Victron connect have a demo library you can play with for that.

Or you can run through a few articles like this one using the generator function on the GX.

https://www.victronenergy.com/live/drafts:acin_ignore_timer_using_ccgx_gen_start_stop_example

Or this one on the inverter itself

https://www.victronenergy.com/live/assistants:ignore_ac_input_using_the_generator_assistant

Your other options are using contactors and relays for commands but is more complex to set up.

21 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duswami avatar image duswami commented ·
Yeah I did some more reading on this. It's confusing between using the virtual switch and setting up the relays. It seems like it's an either or option correct?

My focus is just on prioritizing PV over battery depending on SOC. Aside from the additional complexity is that not possible, or is that something you need to go to Node Red for?

0 Likes 0 ·
Alexandra avatar image Alexandra ♦ duswami commented ·

No. There is more what is convinient and easy for you to set up. And based on what you need.

Conditional AC in Victron Connect is basically Virtual switch in VE Config.

Most people who use the assistant for generator to ignore AC do so because they have other assistants they need/want to use so have to disable Virtual Switch to do so, but still want the function.

0 Likes 0 ·
duswami avatar image duswami Alexandra ♦ commented ·
@Alexandra I see. I was looking at the generator assistant in the Cerbo, is that not the best solution. Incidentally, where is that conditional AC toggle, I can't seem to locate it?
0 Likes 0 ·
Alexandra avatar image Alexandra ♦ duswami commented ·

@Duswami

AC input control in Victron Connect? The manual describes all the settings.

screenshot-20220620-072415.jpg

0 Likes 0 ·
Show more comments
shaneyake avatar image
shaneyake answered ·

Can you explain why you don't want to use ESS? It is normally the best option for cases where you need to use PV.

If you have a Cerbo GX I would use the Large firmware
https://www.victronenergy.com/live/venus-os:large
You can then use NodeRed to fully control your system.
Will need a wire from GX relay to AUX input if you want to control AC OUT2.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duswami avatar image duswami commented ·
@shaneyake Well, technically, I could use ESS, my grid is United States, so I'd have to manually configure with no grid code. Havent found a good thread or guidelines for configuring in the US since it's not supported in ve config. I'm interested in Node Red, but I've been told it's difficult to work with if you don't have programming background.