How to limit feed in power?

I am trying to limit feed in power but with no success.

When I set limit to 0W or any other value:

screen-shot-2022-06-16-at-114342-am.png

System ignores the setting:

screen-shot-2022-06-16-at-114402-am.png

What I am doing wrong?

feed-in limit
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

Hi @MarekP,

My first guess would be the Fronius inverter is not prioritising the reduce output messages sent by the GX device - I would double check the configuration on the Fronius Inverter.

The specific instructions are here -

https://www.victronenergy.com/media/pg/Energy_Storage_System/en/configuration.html#UUID-634c2829-76e8-4e0a-522b-32bbe2cd1c92

Perhaps post a screenshot of those settings as you see them if you believe they are correct.

3 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

marekp avatar image marekp commented ·
@Guy Stewart (Victron Community Manager)

Your guess was correct.

The setting were not correct. I assume they were at default.

My installer probably never touched them.

Good think he gave my the service password. :)

Thank you for a quick response to my question.