Can the Smart Shunt 500 satisfy ESS requirements.

Working on setting up an ESS system and currently have a Smart Shunt 500A ve Direct into the Cerbo. Generally speaking, will this satisfy the battery monitoring requirements for most ESS applications or do I need to upgrade?

System:

Multi II 48v 3000/35 120v

150/45 MPPT

Smart Shunt 500A

Lynxh Dist

Cerbo GX

200Ah AGM bats

1.5 kw Solar

cerbo gxESSBMV Battery MonitorSmartShunt
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
mindaugas avatar image
mindaugas answered ·

I am using it for my ESS and it works. Time to time I need manually readjust SmartShunt based on BMS SOC. What I also found as must is current transformer used on grid input phase wire for ESS to work. I am not feeding back to grid.

victron-setup.png


victron-setup.png (67.1 KiB)
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

duswami avatar image duswami commented ·
Thanks @WKirby @Mindaugas . I didn't want to get another battery monitor, and yes I'm under 500A. I have an EM24 AV6 I will be using as a CT.
0 Likes 0 ·
wkirby avatar image
wkirby answered ·

You can use the 500A SmartShunt in an ESS system, provided your DC current is less than 500A of course.