ET112 Neutral wiring UK Single Phase

Hello,

When looking at the ET112 wiring diagram it shows two ways of which this can be wired. Can the ET112 have the main neutral wired through it like figure 3? My electrician wants to check to make sure these are designed to have the main neutral fed through.

This is the UK and we have a Single phase, 100amp supply fed via 25mm tails after the meter.


et112.jpeg

Many thanks


Energy Meter
et112.jpeg (143.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
dansonamission avatar image
dansonamission answered ·

Ours is wired as per fig 1. Din rail mounted fuse holder.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

jon-young avatar image
jon-young answered ·

My electrician seems to think its really bizzare to fuse the neutral.

7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

dj-dulux avatar image
dj-dulux answered ·

We have done it both ways depending on the layout of the tails. Few things to note, L and N tails must enter or leave a metal enclosure through the same hole which complicates things a little on some enclosures. We generally use a plastic one for this so N goes in and out the bottom, L in and out the top. Using a 32mm tails gland means the earth hole can be used for the data cable.