question

nostromo avatar image
nostromo asked

Why no battery discharge when external current sensor AUX1 is connected ?

Could someone experienced the fact that the external current sensor disable the battery discharging ?

So no power feeding from battery if current sensor is used (ie. To monitor power from another inverter)

sensor
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Jason - UK avatar image
Jason - UK answered ·

@nostromo I had the same issue. It took me weeks to find the answer. In short, there is a setting in VE configure (added after a recent firmware update) that allocated AUX1 to a grid demand interlock. You have to disable this in VE configure but if you have applied a county specific grid setting toy uor VE configure files, you'll need a password from Victron to disable this setting should you want to use AUX1 for the CT sensor.

See below link.

https://community.victronenergy.com/questions/134316/multiplus-2-5kva-48v-gx-issue-with-aux1-with-ct-se.html

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nostromo avatar image nostromo commented ·

@ Jason - UK

Big thanks dear, I'll try this and keep you posted.

Best regards.

1 Like 1 ·
nostromo avatar image nostromo commented ·

@Jason - UK

Hi Jason, I applied your method and it work.

Thanks a lot for support. I really appreciate.

FYI: External sensor assistant don't work after soft reboot of the unit. You must absolutely do a hard reset via ON/OFF button (It’s the case on my unit). I pass hours to find this tip :-)

Best regards.

1 Like 1 ·
nostromo avatar image
nostromo answered ·

@@Alexandra

Can I've the password to change the parameter AUX 1 as disable Feedin signal ?

Best regards

8 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Alexandra avatar image Alexandra ♦ commented ·
@nostromo

I am not able to provide you with that (for legal reasons) since for some it is grid code and therefore compliance related.

For the rest aux is alternatively programmed through assistants and does not need a code.

0 Likes 0 ·