What could be wrong with the settings in the configuration, PV line is not visible. Energymeters? CT?

1654865080533.png

VRM
1654865080533.png (53.0 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
sharpener avatar image
sharpener answered ·

Wrong setup in Energy meters or PV inverters in Device list? The listed position has to be consistent with the physical topology. A schematic would help...

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisvillers avatar image
chrisvillers answered ·

1655100437760.png

thanks a lot, I will check setup


1655100437760.png (65.1 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisvillers avatar image
chrisvillers answered ·

I changed a setting and new PV is ok but the AC load watts is not correct. It changes equal with the PV invertor watts. L1 watts is wrong at the AC loads.

Is the CT measuring the AC loads in the vrm portal? The electrician said he extended the ct with a longer cable. If there is something wrong with ct what will happen?

1655109047757.png




1655109047757.png (56.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisvillers avatar image
chrisvillers answered ·

When pulling out CT then we have the following dashboard : seems a lot better.

So what does CT exactly do? Direction of the CT is ok.

1655113136922.png



1655113136922.png (44.3 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sharpener avatar image
sharpener answered ·

Assuming the two Energy Meters are correctly linked to the Multi the CT is not necessary and will make its brain hurt. The Multi's internal CT is sufficient to measure the current difference going into/out of it.

Plugging in the external one will make it think it is seeing the same thing, but it is actually measuring L1 Grid which is why the calculated load (= Grid In + PV generation - current into Multi) equals the PV reading.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

kevgermany avatar image
kevgermany answered ·

Please check in the advanced menu. Seems to be a VRM problem.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

chrisvillers avatar image
chrisvillers answered ·

thanks, the problem is solved now.