I bought an Rv coming with solar flex 200 and a victron controller 15 amp, the numbers not match with the expectation. The solar is 200w but the controller is showing always that is coming 42 v approx.
Is ok? Should be 24v? Or something is wrong
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
I bought an Rv coming with solar flex 200 and a victron controller 15 amp, the numbers not match with the expectation. The solar is 200w but the controller is showing always that is coming 42 v approx.
Is ok? Should be 24v? Or something is wrong
It sounds like you have two future solutions solar panels connected in series on your roof. Are you certain you don’t actually have the solar flex 400i system?
In any case, you probably have the Victron 75/15 SCC installed. It will allow you to have as much as 75v coming in from your solar panels and will automatically reduce it to your 12v batteries requirements. No need to worry about it but you really need to get up on that roof and double check how many solar panels you have up there. Grab a volt meter and figure out what’s going on.
Perfectly fine. Panels produce higher voltage than the batteries. You'll see the display has panel voltage and battery voltage. Battery voltage is almost reaching 14.4V, perfect under full charge conditions.
Get up on the roof and check the back of the solar panel to see it’s specs. I’m sure you will find that something is different from what you were told you have from what you actually have. It looks like your system is running fine so no need to really worry about this. But if it were me, I’d still want to know what equipment is actually installed.
MPPT 150/60 up to 250/70 Manual
Additional resources still need to be added for this topic
62 People are following this question.