Multiplus-II Wire Size Smaller Than Fuse?

I've purchased a Multiplus-II 24/3000/70, and the manual recommends a 300A fuse, but then only 50mm2 wire size - am I correct in thinking this would be undersized for a fuse of this size?

I'm also wondering if anyone has used a smaller fuse of say 175-200A?

Multiplus-IIfuses
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

1 Answer
kevgermany avatar image
kevgermany answered ·

I'd stick with the recommended size. The start current on the multiplus can be very high as its capacitors charge. If you do get a short, a 300A fuse will blow quickly.

5 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sasunnu avatar image sasunnu commented ·
Thanks. The 50mm 2 wire would be undersized for a 300A fuse though, wouldn't it?
0 Likes 0 ·
kevgermany avatar image kevgermany ♦♦ sasunnu commented ·
Guess it depends how you're using things. Here not.
0 Likes 0 ·
sasunnu avatar image sasunnu kevgermany ♦♦ commented ·

Sorry if my questions are dumb, I'm quite new to this. Do you mean if I am not running the multi to full capacity then 50mm2 would be sufficient? The 50mm2 cables I am looking at have an amp rating of 246 at 30oC, and in all the wire size/maximum amperage charts I have seen 50mm2 is always under 300A.

0 Likes 0 ·