Smart BMS CL 12/100- Persistent A-B11: Under voltage Error

img-20220607-095555-01.jpgPurchased recently a Smart BMS CL 12/100 and connected to boats Lead acid start battery and LiFePo4 service battery. Configured it to use 60A current limit by using 60A fuse, and setting the same in Victron Connect App. But it seems to be a persistent error message I’m not able to clear no matter what I do. Tried “Facory reset”, use “Mode switch” to turn OFF and then ON again, but to no success. Voltages seems to be correct, but no charging of Lithium battery from the alternator, see screenshots attached. Could it be a configuration issue, or something else?

BMSalternator
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

4 Answers
fredivar avatar image
fredivar answered ·

No one have any suggestions or comments?

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fredivar avatar image
fredivar answered ·

This is very strange. Received another Smart BMS CL 12 /100 from my Dealer in Norway, but the new one act exactly the same as the previous one, same A-B11 Under voltage error. No matter what I do, the error is there all the time, even though voltages is at full charge on both battery banks. Firmware V. 1.06


2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

nebulight avatar image
nebulight answered ·

Next thing I would check would be the cables from the batteries to the BMS. Make sure there are no bent pins or connections that are loose. My guess is the BMS isn't getting a signal from the battery that the allow to discharge is triggering a low voltage alarm on the BMS.

Stupid question, but you are using Victron Smart lifepo4 batteries, correct?

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fredivar avatar image fredivar commented ·
Thanks for your comments, your last question is not stupid and I am not using Victron Smart Lifepo4 batteries, but Meritsun 12v200ah battery, so connection to batteries is simple, just the straight connection to batteries/alternator and ground connection. I cannot see from documentation that a Victron Smart Lifepo4 is required? It should be possible to use standard batteries too?
0 Likes 0 ·
Stefanie (Victron Energy Staff) avatar image
Stefanie (Victron Energy Staff) answered ·

Hi @fredivar

The Smart BMS CL is exclusively for Victron Lithium Smart batteries and cannot be used with your battery.

See also the Description in the manual or the Product description.

edit: I just had a look at your battery. It has an internal BMS. So I suggest to read the manual of your battery and see how you can control your devices.

6 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

fredivar avatar image fredivar commented ·

Hi @Stefanie

Thanks for you feedback, I really hoped that this unit was able to be used with other off the shelf LifePo4 batteries, to be able to protect the alternator from excessive heat and possible failures, and if only possible to be used with Victrons own smart LifePo4 batteries, this was really bad news. Is it political by Victron to only support own batteries, or is it electrically impossible because the Smart BMS CL 12/100 only controls the internal BMS inside Victron batteries, not that it actually is able to limit current by itself without the Victron batteries?

0 Likes 0 ·
Show more comments
fredivar avatar image fredivar commented ·

Hi @Stefanie

I read many of the Victron manuals, and especially the Victron Smart Lithium battery where it was thoroughly explained how connection and functionality towards different BMS are. And also read different threads here on the community, and it was eventually obvious to me that the M8 Circular BMS cables needs to form a closed loop either with one or several batteries, and wondered if it would be possible to just make a similar closed loop, but without the Victron Smart Lithium battery in between. So I connected from the Male M8 to the Female M8 signals (through resistors) , and saw that "Under voltage" error disappeared and Charging to Lithium battery started. I find it strange that on many websites that sell Victron equipment, many do not list the M8 Circular BMS cables as "related" to the SmartBMS CL 12 /100 . Since my Lithium battery have its own BMS and protection circuits, I assume I don't need the BMS functionality here, but I would need the Alternator protection circuit in the Smart BMS CL 12 /100, and assume this will still function even though the BMS functionality do not. In my system, the alternator current limit would be around 50A since 60A fuse is in place and also selected in the App.