Good day,
I've connected the energy meter and it shows on the gx, but doesn't display grid power (although the load draws power from grid)
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
Good day,
I've connected the energy meter and it shows on the gx, but doesn't display grid power (although the load draws power from grid)
Did you install compatibile version of EM24?
Did you connect EM24 to your GX controller?
Did you tell GX that you have EM24 as a grid meter?
Show us the EM24 status.
Thanks for the reply, all those boxes are ticked, somethings else is wrong, maybe the meter itself, does it need extra settings?
Which model of the EM24 you have, RS485 or Ethernet?
How it is connected to GX device?
more info here:
https://www.victronenergy.com/live/energy-meters:em24
extended with ethernet cable probably 60m
It shows live voltage per phase but no current
Updated software on gx, changed role to AC load, seems to work now...