Preventing Grid charging

Our sysem will go into sustain mode(batteries are at 40%) and charge form the grid as well as PV in the morning.

How do we prevent if from going charging from the grid at all ?

ESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

2 Answers
Paul B avatar image
Paul B answered ·

When using Ess assistant set the Grid setpoint to say 50w

I also Open and close the AC1-in when I dont need the grid so that Freq shift will work on my Grid tie inverter, so it turns OFF when the batteries are full

plus I also do the Below in conjunction with a ccgx and generator Autostart, the Autostart makes AUX1 Hi or Low using the relay on the CCGX triggered by the Generator Autostart parameters

I am using a grid Tie inverter connected to the AC1 out of my Multiplus 48/5000 unit.




1554286743252.png (28.5 KiB)
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

boekel avatar image
boekel answered ·

Your batteries are below the sustain voltage, so you have to lower the sustain voltage to prevent charging.
I assume you have lithium batteries?