A bit new to this so apologies in advance.
Equipment:
MultiPlus II 48/3000 35 120v
SSCC MPPT 150/45
Lynx Dist
SmartShunt
4 x 12v 200ah lead acid bats (48v)
Solar array output 1480w 96v 20amp
So I thought I had fusing with the lynx distributor and breaker sizing for the Multiplus all figured out, but doubting myself again.
First, fuse sizing the battery, charge controller and inverter at the lynx distributor.... I figured if the inverter with power assist runs at the full 3000w off my 48v batteries it draws approx 62 Amps. So, I'm thinking 60+ amp fuse is correct for the battery, CC and inverter??? The inverter manual states that the max charging current is 35 Amps. Consequently, on the AC side, I have a 60amp breaker for both the AC IN and AC OUT in the service panel. But after reading endless posts I'm doubting myself. Anyone see anything off here?