question

Alex Manley avatar image
Alex Manley asked

Quatro 15 kW UPS system - Ii it approved for AS 4777.2

Hi Guys

I'm reading that the Victron inverters are not approved under AS4777.2 for grid connection (ESS).

Dose this apply if its just setting up a 15 kW Quatro as a UPS system and not wanting to export energy to the grid ?

Can i still get STCs if i connect a fronius inverter on the output side of the Quatro, as its approved and would help charge the batteries in off grid mode.

Thanks for your help in advance.

ESSups
1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Rob Duthie avatar image Rob Duthie commented ·
Hi


These are not approved for 4777.2 2020 only the Multiplus2 2-5Kw under Appendix M certificates, can be used in a certain way.

As the law stands 4777.2.2015 still would apply as not ratfied into law yet.

The only way to do that is use a grid protecion relay like a Tele or ComAp device. at a aprox cost of $1000.

Regards

Rob D

NZ

0 Likes 0 ·