PeterM asked

Solar radiation sensor

Anyone come across a solar radiation sensor with output voltage proportion to incoming insolation. Would like to record the values with the Venus GX.

Venus GX - VGXsolar
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

7 Answers
Guy Stewart (Victron Community Manager) avatar image
Guy Stewart (Victron Community Manager) answered ·

UPDATE - We now have a resolution!

The Si-RS485TC Series solar irradiation sensor and optional wind and temperature sensor are now natively supported by GX devices.

See here for more information on wiring, configuration, and output:

https://www.victronenergy.com/live/ccgx:start#connecting_imt_solar_irradiance_temperature_and_wind_speed_sensors

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

wkirby avatar image
wkirby answered ·

Yes, it's called a solar panel! :)
Seriously though, sensors like that are just miniaturized PV modules (the same chemistry) with a constant load or resistor across them. The voltage output is then proportional to the light intensity.
Often, a small solar panel is used as the sensor in DIY arrangements.
Someone in this community did do something with the Venus' temperature inputs to measure insolation. I'll hunt around for the link and post it here.

2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Pat Davitt avatar image
Pat Davitt answered ·

I am not familiar with the term "incoming insolation", would someone please explain.

I'm using a Solar Irradiance/Panel Temperature sensor from IMT Solar for my diversion load project. It returns irradiance in W/Meter Squared and panel temperature in degrees C. They are available with 0-5V, 0-10V, or 4-20mA outputs. Don't know if it could interface with the Venus GX, just thought I would mention it.

Pat

2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

PeterM avatar image PeterM commented ·

also called irradiance see https://en.wikipedia.org/wiki/Solar_irradiance , I'll look up that sensor thanks


0 Likes 0 ·
Pat Davitt avatar image Pat Davitt PeterM commented ·

Thanks for the info. The IMT Solar sensor model I am using is Si-I-420TC-T.

Pat

0 Likes 0 ·
tilo avatar image
tilo answered ·

I have a small solar panel (3W for 6V batteries, about 0,3A Imp) connected to the Venus GX tank level input, together with a 2,2 Ohm resistor in parallel. The Tank Level input is configured for 0-180 Ohm tank level sensors. The graphic below looks as one would expect a solar radiation curve.

The calibration could be done in comparison with the actual solar generator. One easy option for calibration is that the tank level indicates the same number as the PV output, for example 1800 liters means 1800W. Adjust the tank capacity till PV yield has the same number as Tank Level. Like this it is easy to read how much PV power is available versus how much is actually used.

The calibration with the PV generator should be done during "bulk" phase, when the charge regulator is not reducing PV output.

If you prefer the figure representing solar radiation as W/m2, do the calibration above first, then divide the tank capacity by your kWp solar generator size. Maybe add something for the reduced efficiency of the PV panels at higher temperatures than 25 C. Or do the calibration when the PV panels are at 25 C on a cloudy day.

Another way of calibrating is to measure the short circuit current of a PV panel and compare to its Isc maximum current according to its label. Be aware, small panels (2W, 5W etc) which could be used as sensor may be very inaccurate in terms of label and real performance, better use a big "serious" panel for calibration if you want more precision.




7 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Pat Davitt avatar image Pat Davitt commented ·

Interesting, I like where you are headed. You might consider measuring the Open Circuit Voltage (Voc) of the panel; it is directly related to the solar irradiance the panel is receiving. You can then compare this to the STC ratings of the panel and compute the wattage output for any given any sun condition. That's what, I believe, the IMT Solar sensor does.

Pat

0 Likes 0 ·
PeterM avatar image PeterM Pat Davitt commented ·

Nice solution -what you need to also do is try and factor out panel degradation. Thats ultimately what I want to do so you need a sensor with a well characterised degradation curve

0 Likes 0 ·
boekel avatar image boekel ♦ Pat Davitt commented ·

Voc is related to temperature, not the amount of sunlight

Current is related to the amount of light, that's why Tilo's solution works with the resistor in parallel.

0 Likes 0 ·
Pat Davitt avatar image Pat Davitt boekel ♦ commented ·

You are correct, Voc measurements do need to be temperature compensated. However, Voc is linked to solar irradiance.
For this to work the following conditions must be met:

1. No loads can be attached to the measurement panel.
2. A very precise voltage measurement device must be used.
3. A panel temperature measurement device must be provided.
3. A means of mathematically calculating W/M2 from the voltage measurement and Voc temperature coefficient must be provided.
4. The sensor device must be calibrated using STC test equipment.

In the graph shown below there is a large jump in Voc between 0 and 100 W/M2 and then the Voc increases linearly, in small increments, with Irradiance.
Also below is the Calibration Certificate for the sensor I am using.

Pat

0 Likes 0 ·
Show more comments
PeterM avatar image PeterM commented ·

YEs good idea, need to factor out how to set the tank inputs on Venus


0 Likes 0 ·
Lionel SEYDOUX avatar image
Lionel SEYDOUX answered ·

@Pat Davitt

Nearly all the answers I need. But being a newbee in Victron's maze, I would appreciate further guidance to have the irradiation info on VRM.

I think someone wrote here that Victron was considering a special accessory for that, probably to be plugged into CCGX VE-CAN or somewhere else. No new as of now.

For that limited purpose something like a Si-RS485TC-T or 2T should do (I shall check with imt-solar) but how to feed it into CCGX, to have the result on VRM? Can Tank Sender adapter?

For some years I had a voltage logger (EL-USB) measuring the voltage between the ends of a resistor fed by an old 20Wp. setting was done by adjusting the R value. But it was cumbersome (offline management, no temp correction...). A solution throu CCGX and VRM wouls be fine!

Thanks

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Hi @Lionel SEYDOUX

Good news: there is (beta) support for a standard sensor, read here:

https://community.victronenergy.com/questions/31299/venus-os-v24034-available-for-testing.html?

0 Likes 0 ·
Lionel SEYDOUX avatar image
Lionel SEYDOUX answered ·

To Guy Steward,

Nearly all the info I need. Just not to lose time whan I purchaseans install a Si-RS485 TC -T

- Is the output cable from the sensor nude or fitted with a RS485 plug?. That would meant I should purchase a RS485 femele to female plug. On the connection drawings you send it looks as if both sensor cable and RS485 to USB cable have to be denuded and connected in some sort of connecting box. Am I right?

- About the version of Venus OS, on VRM I have for Gateway, firmware V 2.52 is that OK?

Not in my mountain yet: too much snow and the lifts are closed.

Good luck to you and all colleagues!

Lionel SEYDOUX


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

Mark avatar image Mark ♦♦ commented ·

Hi @Lionel SEYDOUX,

-RS485 is not a 'plug' standard/description - it is a standard related to the electrical characteristics of drivers and receivers in serial communication systems.

-Both the IMT Si-RS485TC Series irradiance sensor and the Victron RS485 to USB interface cable come with bare/stripped wire ends - see photo below;

-You can join the wires together directly with a single terminal block if you have enough length. But if you need more length, simply use an appropriate specification data cable to extend it and use two terminal blocks.

As the wires are so small/fine, its a good idea to use small bootlace terminals on all ends.

Also include a small inline fuse (~1A max) on the DC power supply.

-Venus OS FW v2.52 is fine, the update was introduced in FW v2.40.

Best of luck with your install.

0 Likes 0 ·
Lionel SEYDOUX avatar image Lionel SEYDOUX Mark ♦♦ commented ·

Thanks Mark

Suite clear now! On my roof as soon as possible!

0 Likes 0 ·
albertvanheerden avatar image
albertvanheerden answered ·

Good day,