sascha-brinkmann asked

Warning "Low battery voltage" at high load

I'm operating a 4,8kW Peak PV System with a Huawai Inverter. Recently I've added MultiPlus-II 48/3000/35-32 GX with a 175ah Battery. A Victron Energy Meter ET340 measures the residual load and provides the information to the victron.


I'm operating the MP 2 with ESS to charge the surplus of the PV system into my battery or to level my grid demand to zero to the extend it is possible. When I'm charging my electric vehicle with 6 kW, I'm utilizing the PV system and MP 2 at the maximum possible power supply.

At this load level the MP 2 is quite unreliable. For a short period it works as expected until the voltage and current drops until discharging starts again (see Video)

Charging is not effected and works as expected at the same rate.

This warning is shown in the notifications

bildschirmfoto-2022-05-19-um-125057.png

Multiplus-IIESS
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

3 Answers
Alexandra avatar image
Alexandra answered ·

What nominal or continuous current rating is the bms?

It is the bms shutting the system down not the other way around.

40A setting is a lot close to the 37A you are drawing out (discharge current limit on bms)


2 comments
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sascha-brinkmann avatar image sascha-brinkmann commented ·
This seems to solve the issue. I've just increased the discharge current on the BMS and now it seems to discharge quite stable. Thanks for the crosscheck. I've overseen this setting!
0 Likes 0 ·
Show more comments
klim8skeptic avatar image
klim8skeptic answered ·

You are still operating your grid tied inverter on a different phase as to your multiplus is operating.

1 comment
2 |3000

Up to 8 attachments (including images) can be used with a maximum of 190.8 MiB each and 286.6 MiB total.

sascha-brinkmann avatar image sascha-brinkmann commented ·
This is just the drawing. In the meantime, I switched to the same phase. For charging the surplus from the PV system it is helpful to be on the same phase. For utilizing PV and battery at the same point of time to charge for example you electric vehicle you're running into the issue that you're breaking the regulatory for phase dysbalance. In Germany you have to take measures that your dysbalance is not exeeding 20A or 4,6 kW. When you're MP 2 and your PV system are operating at their maximum power at the same phase you're exeeding this value. Operating them on different phases prevents violating this regulatory.
0 Likes 0 ·
sascha-brinkmann avatar image
sascha-brinkmann answered ·

Settings from my Dali BMS

screenshot-2022-05-19-13-18-04-442-cominukerblueto.jpgscreenshot-2022-05-19-13-18-11-334-cominukerblueto.jpg