How to display a negative power out on the overview as this photo shows? I'd like to display the AC output power instead the AC loads, which as shown cant be negative.
Thanks a lot in advance.
This site is now in read-only archive mode. Please move all discussion, and create a new account at the new Victron Community site.
How to display a negative power out on the overview as this photo shows? I'd like to display the AC output power instead the AC loads, which as shown cant be negative.
Thanks a lot in advance.
@h3lix As far as I am aware, the value of the AC loads is a calculated figure taking form the measured current on ACin along with the power output from the inverter. I dont think i has a specific way of measuring the AC out unless you add a meter to the AC out. I (when it is working) have a current senor on my PV AC feed which then shows my laods in its calculated value after subtracting the solar generation.
Click on the below YouTube link should both versions of VRM, let me know if this is what you mean.
https://youtu.be/a0QXKCuvZn4
Watch the 2nd half of the video.
Loads can not be negative as they are loads.
It looks like you have a PV inverter on the output of the inverter. That PV inverter needs to communicate to the GX if it can't communicate then you will need to install a meter on the PV inverters output so that the GX knows that the PV inverter is outputting and is able to calculate your loads.